2nd January 2007 at 15:11 #46394
Patrick
GuestBCF-035 ENVIR 2006-11-20 15:02:25.88
* ALARM
(17125) 7602 BCF NOTIFICATION
Cooling fan is broken.
06 02 01 9E 00 00BCF-035 ENVIR 2006-11-20 15:03:41.39
* ALARM
(17127) 7602 BCF NOTIFICATION
Cooling fan is broken.
06 02 0C 9E 00 00I have 2 alarms on the coling who doesn’t exist in BTS.
I have a ultrasite IBBU. (ultra 222 and energy on cabinet, CCUA+Battery)
1st part =>TRX 222
2nd part => Energy (CCUA + battery)My problem is my 2 cooling fan doesn’t exist because it is energy (CCUA + battery)
My SW is ok, commissioning ok.
Who has the same problem? or the solution?
thx.
4th January 2007 at 09:26 #46395Pavel
GuestThis is alarm, which comes from RBS cabinet, not energy.
You should check all cooling fans at the Ultra cabinet. Also, this alarm can come, if speed of fan is decreased.
Additionaly, this alarm can happens if you load ULTRA-MACRO BTS software into ULTRA-MIDI BTS. MIDI BTS have no some fans, that MACRO have. In this case- you will have fan alarm.
4th January 2007 at 11:06 #46396patrick
GuestLook at this, if you see a mistake =>
SW Versions
***************File Name Running Package
————————————
VBO_S305.16D 4. 0.21
PUC_S305.163 4. 0.21
PDI_S305.164 4. 0.21
PDE_S305.165 4. 0.21
PEI_S305.166 4. 0.21
CFG_S305.16F 4. 0.21
RTC_S305.16C 4. 0.21
EC0_S305.167 4. 0.21
EC1_S305.168 4. 0.21
ECE_S305.169 4. 0.21
EE0_S305.16A 4. 0.21
EE1_S305.16B 4. 0.21
BTS_C327.393 4. 0.21File Name Newest in Flash
————————————
VBO_S305.16D 4. 0.21
PUC_S305.163 4. 0.21
PDI_S305.164 4. 0.21
PDE_S305.165 4. 0.21
PEI_S305.166 4. 0.21
CFG_S305.16F 4. 0.21
RTC_S305.16C 4. 0.21
EC0_S305.167 4. 0.21
EC1_S305.168 4. 0.21
ECE_S305.169 4. 0.21
EE0_S305.16A 4. 0.21
EE1_S305.16B 4. 0.21
BTS_C327.393 4. 0.21File Name Oldest in Flash
————————————
VBO_S304.31D 3. 3.18
PUC_S304.313 3. 3.18
PDI_S304.314 3. 3.18
PDE_S304.315 3. 3.18
PEI_S304.316 3. 3.18
CFG_S304.321 3. 3.18
RTC_S304.31C 3. 3.18
EC0_S304.317 3. 3.18
EC1_S304.318 3. 3.18
ECE_S304.319 3. 3.18
EE0_S304.31A 3. 3.18
EE1_S304.31B 3. 3.18
BTS_S305.111 3. 3.18***************
HW Versions
***************Unit Type Version Serial Number
——————————————————————–
BCF BOIA 106 L1023143465
Power 1 PWSB 103 A7022914120
Duplexer 1 DVDC 101 2K023302429
Duplexer 2 DVDC 101 2K023302422
Duplexer 3 DVDC 101 2K023302443
BB2 1 BB2F 102 L1044923997
ETRX 1 TSDB 206 L6050147331
BB2 2 BB2F 102 L1044923992
ETRX 3 TSDB 206 L6050147342
TRX 4 TSDA 110 L6031048997
BB2 3 BB2F 102 L1044924000
ETRX 5 TSDB 206 L6050147308
ETRX 6 TSDB 209 L1063309436
TRE 1 FXC E1T1 N/A 4 4H023210528********************
LAPD Link Status
********************LAPD Link Status
—————————
OMUSIG On
TRXSIG1 On
TRXSIG3 On
TRXSIG4 On
TRXSIG5 On
TRXSIG6 On**********
Alarms
**********Severity Code Time Event Object State
——————————————————————————–
Minor 7602 20/11/06 14:20:18 Start BCF (Unit fan/6/2/1)Enabled
BCF NOTIFICATION: Cooling fan is broken.
Minor 7602 20/11/06 14:20:18 Start BCF (Unit fan/6/2/12)Enabled
BCF NOTIFICATION: Cooling fan is broken.
Minor 7622 20/11/06 14:20:18 Start BCF (BOI/2/1/7) Enabled
CABINET OPEN: Cabinet door is open.
Minor 7801 20/11/06 14:20:18 Start BCF (BOI/-/-/-) Enabled
MMI CONNECTED TO BASE STATION:*********************
Object Properties
*********************Property Value
—————————–
Object BCF
Operational State Supervisory
BCF ID Not defined
Site ID
Site Name
IP Address Not defined
Network ID Not defined
BSC ID Not defined
OMUSIG On
Oscillator State Ready
Clock Sync. State Not Used
Blocked State UnblockedProperty Value
—————————–
Object ETRX 1
Operational State Supervisory
Power Control Range (steps)15
TX Power Level 50000 mW
Network Type GSM 1800E
Commissioned Yes
ARFN 826
Device Existence OK
Locked State Unlocked
Blocked State Unblocked
TRXSIG1 On
IDD Usage Not in useProperty Value
—————————–
Object ETRX 3
Operational State Supervisory
Power Control Range (steps)15
TX Power Level 50000 mW
Network Type GSM 1800E
Commissioned Yes
ARFN 781
Device Existence OK
Locked State Unlocked
Blocked State Unblocked
TRXSIG3 On
IDD Usage Not in useProperty Value
—————————–
Object TRX 4
Operational State Supervisory
Power Control Range (steps)15
TX Power Level 50000 mW
Network Type GSM 1800
Commissioned Yes
ARFN 875
Device Existence OK
Locked State Unlocked
Blocked State Unblocked
TRXSIG4 On
IDD Usage Not in useProperty Value
—————————–
Object ETRX 5
Operational State Supervisory
Power Control Range (steps)15
TX Power Level 50000 mW
Network Type GSM 1800E
Commissioned Yes
ARFN 813
Device Existence OK
Locked State Unlocked
Blocked State Unblocked
TRXSIG5 On
IDD Usage Not in useProperty Value
—————————–
Object ETRX 6
Operational State Supervisory
Power Control Range (steps)15
TX Power Level 50000 mW
Network Type GSM 1800E
Commissioned Yes
ARFN 820
Device Existence OK
Locked State Unlocked
Blocked State Unblocked
TRXSIG6 On
IDD Usage Not in use**************************
Abis Connection Status
**************************Abis enabled
************************
Sector Configuration
************************Sector 103
Hopping Mode: None
Network Type: GSM 1800E
ETRX 1 ARFN:826
Sector 104
Hopping Mode: Synthesizer
Network Type: GSM 1800(E)
ETRX 3 ARFN:781
TRX 4 ARFN:875
Sector 105
Hopping Mode: Synthesizer
Network Type: GSM 1800E
ETRX 5 ARFN:813
ETRX 6 ARFN:820*********************************
IDD Configuration Information
*********************************TRX ID IDD Mode Partner TRX 4UD used
————————————————————
ETRX 1 – – –
(TRX 2) – – –
ETRX 3 – – –
TRX 4 – – –
ETRX 5 – – –
ETRX 6 – – –
(TRX 7) – – –
(TRX 8) – – –
(TRX 9) – – –
(TRX 10) – – –
(TRX 11) – – –
(TRX 12) – – –**************************
Clock Control Settings
**************************State Ready
Current DAC 1962
Permanent DAC 1964**************
EAC Inputs
**************Input 1: Closed
Input 2: Closed
Input 3: Open
Input 4: Closed
Input 5: Closed
Input 6: Open
Input 7: Open
Input 8: Closed
Input 9: Open
Input 10: Open
Input 11: Open
Input 12: Open
Input 13: Open
Input 14: Open
Input 15: Open
Input 16: Open
Input 17: Open
Input 18: Open
Input 19: Open
Input 20: Open
Input 21: Open
Input 22: Open
Input 23: Open
Input 24: Open******************************
BB2 – TSx Cross-connection
******************************BB2 TSx TRX ID
——————————————–
BB2F 1a TSDB 1 TRX 1
BB2F 2a TSDB 3 TRX 3
BB2F 2b TSDA 4 TRX 4
BB2F 3a TSDB 5 TRX 5
BB2F 3b TSDB 6 TRX 6
Upgrade path
BB2F 1b (TSxx 2) TRX 2
(BB2 4a) (TSxx 7) TRX 7
(BB2 4b) (TSxx 8) TRX 8
(BB2 5a) (TSxx 9) TRX 9
(BB2 5b) (TSxx 10) TRX 10
(BB2 6a) (TSxx 11) TRX 11
(BB2 6b) (TSxx 12) TRX 12
(Units in brackets were not autodetected.)******************
TSx RF Cabling
******************TSx TX RX Main RX Div
————————————————————-
TSDB 1 DVDC 1a DVDC 1a DVDC 1b
TSDB 3 DVDC 2a DVDC 2a DVDC 2b
TSDA 4 DVDC 2b DVDC 2a DVDC 2b
TSDB 5 DVDC 3a DVDC 3a DVDC 3b
TSDB 6 DVDC 3b DVDC 3a DVDC 3b
Upgrade path
(TSxx 2) DVDC 1b DVDC 1a DVDC 1b
(Units in brackets were not autodetected.)*******************
Antenna Cabling
*******************Antenna MHA Type Connected To Attenuation VSWR Mon.
——————————————————————————–
1 None DVDC 1a High gain No
2 None DVDC 1b High gain No
3 None DVDC 2a High gain No
4 None DVDC 2b High gain No
5 None DVDC 3a High gain No
6 None DVDC 3b High gain No5th January 2007 at 07:42 #46397Pavel
GuestIn “Sector configuration” you can see, that you BTS is configured like MIDI (max 6 TRXs). But in “BB2 – TSx Cross-connection” i see, that maximum configured TRX can be up to 12.
I have no big practice in BTS, cause I am BSC engenier, but I think that is mistake.
Clarify, which type of cabinet you have.
11th January 2007 at 15:47 #46398patrick
GuestMidi BTS is normal because it is divised into 2.
1 part of 6 trx + 1 part of power (battery+rectifier)
Normally, my BTS mustn’t see cooling fan of power part because it is doesn’t exist.
23rd April 2007 at 13:17 #46399Zayyat
GuestDear Patrick – Dont disturbe urself from the alam address which is:
06 02 01 9E 00 00Its clear that u have a broken cooling fan BEHIND the First Duplixer, replace it.
3rd May 2007 at 10:16 #46400Patrick.fr
GuestI found the solution:
cooling fan are not broken.
If alarm come on the cooling fan 12 (6/2/12) on IBBU BTS ultrasite, the problem is on the CCUA Q1.
CCUA can be 2 adress: 4085 or 4084.
PSM manager => climatic control => FAN.
the CCUA must see 9 cooling fan with the good Q1 adress.
I don’t know explain but CCUA and BOIA are the same Q1 Bus for the climatic control.Problem is over.
22nd November 2011 at 14:49 #46401rahul
Guesthi
there is any option in ultra bts
that cooling fan broken alarm clear by loop only
no need to replace hardware -