RBS6102 – Fault Code description.

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #66167
    Squid
    Guest

    Hello all,

    Can anyone help me with fault code description?
    I have BTS_INTERNAL OPER FAULT=2A-71 on one new installed RBS6102.

    Than you.

    #66168
    patrick
    Guest

    SO CF I2A:71 – Low Battery Capacity
    Description An alarm is raised if the voltage is too low during
    intermittent charging. The battery voltage reached the
    set limit while the battery was disconnected during
    intermittent charging.
    Battery capacity is lower than expected. The backup
    time at the next AC power failure is likely to be shorter
    than expected.
    Action Follow the instructions below until the fault is resolved.
    • Check that the voltage for intermittent charging,
    IDB parameter IntermittentChargeConnectVoltage,
    is set correctly.
    • Check the battery condition, for example, by
    performing an on-demand battery test.
    • Check the condition of the battery and replace it if
    necessary.